Using 8.1.47, PLC is a Siemens S7-1518. The customer is handling the PLC and was advised by IA tech support that people often setup the OPC-UA on the PLC and then the tags become browsable to Ignition.
That works and the tags read correctly.
But I took a look at the tag and I saw this as the OPC Item Path
nsu=
http://www.siemens.com/simatic-s7-opcua;s="Stall01"."StartDateTime"
Never seena url in OPC Item Path before. I tried it a few more times with other tags and same story. Is this expected/normal/acceptable or something worth troubleshooting? Perhaps they configured something poorly ont he PLC OPC side?