I am new to ignition and am still running the trial version for R&D. However, I have hit a snag. Per the User Manual, I should be able to access all the Extended Memory areas of the PLC. I get a Bad quality and value showing on the tags created for E memory areas E10 through E18. There are no issues with E00 through E0F. Any help in this area would be a great help.
Okay, according to the FINS spec/manuals this means:
A correct memory area code has not
been used or Expansion Data Memory
is not available.
Can you get a Wireshark capture of one of these reads? I'm not sure how else to verify that the correct memory area code is being used. Otherwise it means these memory areas aren't available for some reason.
I downloaded Wireshark. I have attached a screenshot of the PLC memory area map showing the usage of the EM addresss.
It only gives this error when accessing E10 to E18 memory areas. Setup of address areas appears to be the same, but I am not sure if I have the structure correct.
Can we focus on one single address in an EM area that doesn't work? Every screenshot you've showed me has been something different. I can't correlate logs to wiresharks to configuration if you keep jumping around.
Turn that logger to DEBUG, start a Wireshark capture, browse to an EM tag in the OPC Quick Client in the Ignition Gateway and do an explicit read. Note the address, make sure you see a corresponding error in the logs for that same address, then stop the capture.
Well, I think this could be a bug in Ignition, I'm going to ask QA if we have any of the PLCs set up with EM at 0x10+ and see if it's broken for us as well.
It would still be useful if you could attach or DM me that Wireshark capture.
I am not able to read decimal/float values for my EM Area address E301332 and ED3602. While creating tags in ignition I am using E031332 and E133602 respectively. I am expecting float values but getting int values.
Maybe you need to use one of the byte/word order modifiers. Float and double span multiple native 16-bit EM registers, so the ordering is whatever your application / PLC program decided to do.
Ok. What I am expecting is 0.34 and 1.00 instead of 34 and 100. Using modifier how my address will look like. Could you please help me out with one my tag? E03float@HL1332 is this correct?