hi, i am facing the below issue.
i have connected 20 Omron FINS devices in ignition gateway and total of 134 other device configuration.
i am facing frequent reconnectwait issue . some of the devices are connected and some are showing reconnectWait issue.
In logs i found the following error.
Any solution for this would be appreciated.
You may find this thread of interest.
Hi All, I’m using edge 8.1.7 with OPC UA Omron FINS/TCP connection.
On the Status>Connections>Devices page, it shows overloading of PLC.
The write/sending of values to the plc is instantaneous, but the reading from PLC to gateway is slow. Having delay of 3-6++ seconds.
While reading the OMRON FINS Driver manual, it mentioned about FINS Settings and Request Optimization.
For FINS Settings, right now all the values are default:0 in the configuration.
But on the actual PLC, we have tuned the…
1 Like
Can you get and share a Wireshark capture?
Are you setting "Source Node" to something other than 0 for your devices?
Source node is Ignition Last two IP number
Destination node is PLC last two IP number