On Gateway Restart, all active alarms return to Un-Acknowledged

I am noticing that whenever I restart the gateway, every active alarm becomes un-acknowledged even if it had been acknowledged prior to the restart. Is there a tag or alarm configuration setting that I am missing here that would stop this from happening? Haven't been able to find any documentation on this or past forum posts.

Any help would be appreciated.

Hi @Nate_Lobik,

On the Gateway you can visit Config > Alarming > General to see some of the global alarm config settings. One of these is "Continuous Event Detection Window" which I believe is involved with retaining alarm events through a Gateway restart.

For Ignition 8.1 this is documented here:

https://docs.inductiveautomation.com/display/DOC81/Gateway+General+Alarm+Properties