December 12, 2019, 11:26pm
1
I am creating a connection on an 8.0.6 ignition to another ignition server running 7.9.12
GIF steps
Endpoint Discovery
Choose A Server
Security setup
Left auth blank
I created a new Client cert on the 8.0.6
I then applied this to the 7.9.12 server
But the OPC Connection on 8.0.6 server shows Faulted.
Can someone point me in the right direction here?
Are these two servers running on the same machine? Your GIF shows you connecting to localhost…
And whatever you’re doing with that client certificate isn’t necessary. 7.9.x doesn’t have any kind of certificate handling.
jpence
December 13, 2019, 12:37am
3
No, not on the same server. I don’t see the localhost you refer to. The gif shows 127.x.x.x not localhost.
I was trying to follow the Kepware OPC connection article. Is there an article on how to connect one ignition opc ua server with another ?
pturmel
December 13, 2019, 1:18am
4
Say what? 127.x.x.x is defined (By IETF) to be only valid for localhost. It is never valid for anything else.
jpence
December 13, 2019, 2:37am
5
Ah. Not an expert network guy here. That explains why I got so far.
I kept on using the IP address of the machine and it wasn’t working ( error code to follow) so I did a netstat in power shell to look for which IP address was associated with port 4096… and yeah 127.x.x.x came up.
Back to the drawing board
jpence
December 13, 2019, 2:04pm
6
Here is the remote server, IP address 10.64.61.151, showing port 4096 for the OPC-UA service
when i try to connect from the main, I get this error
pturmel
December 13, 2019, 2:42pm
7
Connection Refused is typically due to a firewall along the way.
Or in this case, because the other server is clearly configured to bind to “localhost”.
Replace “localhost” in that configuration with the IP (10.64.61.151?) of that server and then restart Ignition.
If you don’t manage to get this working soon support would be able to walk you through it pretty quick. Just make sure you call, not email.
1 Like
jpence
December 13, 2019, 3:04pm
9
Thank you Phil and Kevin
I changed the Endpoint Address to 10.64.61.151 and restarted the Ignition Gateway service
I then went back to the other server and attempted to connect again with the same result.
I’ll give support a call.
jpence
December 13, 2019, 7:33pm
10
Joe R in support helped me out here
The server and client certs on the remote side were wrong ( had odd looking ip address)
Once we fixed that I was connected