OPC-DA server

Hi.
I have a problem with OPC-DA server NewronSystem NLopcTE. I don’t see any tag in Ignition tag browser. This OPC server gets information from Lon device.

Being that this is an OPC-DA Server:

– Do you have the OPC-COM Module installed on the gateway? It sound like you probably do, but just making sure. :wink:

– Do you have any tags set up on the NLopcTE Server?

Any extra details you can give may help us help you. :smiley:

I have OPC-COM module and I can read all tags from the OPC server using other OPC-client.

I’m going to jump over to your other post. That way we can pool our resources a bit. :slight_smile: