OPC Tags Fail After Importing Tag Groups Between Tag Providers (8.1.52)
I am encountering an issue when exporting and importing tags between Tag Providers on the same Gateway.
Scenario:
  • Ignition version: 8.1.52
  • Same Gateway (Export/Import so both tag provider access same device)
  • Exported from one Tag Provider and imported into another for demo/testing purposes
Export contents:
  • Tag Group(s), UDT Definitions, Tags
Steps performed:
  1. Exported Tag Groups, UDTs, and Tags from the source Tag Provider.
  2. Imported them into the target Tag Provider in the following order: Tag Groups, UDT Definitions, Tags
Issue observed:
After the import, none of the OPC tags subscribe or update. No OPC values come through. Additional observations:
  • If I change the affected tags to use a newly created Tag Group, they immediately begin working!!!
  • If I delete the imported Tag Group and recreate it with the same name, the tags still do not work.
  • This suggests the tags may be referencing an internal Tag Group identifier that is no longer valid after import.
Expected behavior:
Imported tags should correctly bind to the imported Tag Group (or rebind by name), and OPC subscriptions should function without requiring manual reassignment.
Could anyone confirm whether this is a known issue in 8.1.x, and if there is a recommended or supported workflow for moving tags between Tag Providers on the same Gateway?
Hmm. I haven't heard this one. You should open a support ticket.