OPC-UA Allen-Bradley ControlLogix 5500 driver

How do you add tags to the OPC-UA Allen-Bradley Controllogix 5500 Driver? We have an Allen-Bradley PLC up and running. I added it as a device and it shows that it is connected in the Ignition Gateway, but when I use the Quick OPC client I don’t see any tags.

Which version of Ignition are you running? If not version 7.0.2, please download it from our website. Also, we will be releasing an update in the next couple of days that includes more fixes in the driver module.

Thank you,

Tom

I updated to 7.0.2, which appears to have resolved the problem.