Hello @Kevin.Herron , Can you please help with this issue.
We are trying to establish the OPC-UA connection between Ignition gateway and Siemens PCS7 v9.0.
Got the error Bad_SecurityChecksFailed .
Attached the error log.error.txt (2.2 KB)
Can anyone help me with the error message?
Ignition OPC configuration:
Security policy: Basic256sha256
Security mode: Sign&Encrypt
Ignition has accepted the certificate from siemens wincc.
Siemens side configuration
Security policy: Basic256sha256
Security mode: Sign&Encrypt
Since there is no option to accept the ignition client certificate, we have copied to the specific location in the siemens server.
Server endpoint selection:
Certificate trusted
Connection error
It looks like you’ve done all the things you’re supposed to do and WinCC is still sending back the Bad_SecurityChecksFailed error. You’ll probably have to contact Siemens support if you can’t figure out how to get more information about why.
Hello @Kevin.Herron ,
Thanks for the reply
Have you checked the error log attached?
error.txt (2.2 KB)
Yes, the error is how I know it’s coming from the server and not being generated client side.
1 Like
Thanks, @Kevin.Herron ,
Suspected the same. Raised a request with siemens.
zxcslo
February 1, 2021, 7:41pm
6
Have you tried completely compile the PCS7 project and downloading it again?
Hello all,
We are able to rectify the issue. We found there are 2 root causes
Wincc connectivity pack license not available
OPC-UA client (ignition) should authenticate against the windows credentials of WinCC station.
Thanks for your support!
Regards,
Saravanan.