OPC UA Connection to Schneider Modicon M241 - Connection Rejected

Have a Schneider M241 that was happily communicating with Ignition for some time and then after a power cycle of the M241, just decided to stop communicating.

UaException: status=Bad_ConnectionRejected, message=io.netty.channel.AbstractChannel$AnnotatedConnectException: Connection refused: no further information: /10.80.58.1:4840

We have a ton of other devices that are still communicating OPC/UA so doesn't look like a Module issue.

Have configured and reconfigured and configured again on the M241, tried changing ports on both ends, still get connection refused.
OPC UA Server Configuration (schneider-electric.com)

connectionRejected-DiscoveryServerLookupStep.txt (9.1 KB)

Have posted to Schneider forums without response so figured I'd give it a shot here.
Thanks in advance for any suggestions.

Here's a section from the OPCUA Configuration settings file:

[Endpoints]

Endpoints/size = 2

Endpoints/0/EndpointURL = opc.tcp://0.0.0.0:4840

Endpoints/0/BindURL = opc.tcp://0.0.0.0:4840

Endpoints/0/SecurityPolicies = SecurityPolicy_None

Endpoints/0/UserTokenPolicies = Anonymous,UserName

Endpoints/0/PKIStore = PKIStore_None

Endpoints/0/TrustAllClientCertificates = false

Endpoints/0/DisableErrorCertificateTimeInvalid = true

Endpoints/0/DisableErrorCertificateIssuerTimeInvalid = true

Endpoints/0/DisableErrorCertificateRevocationUnknown = true

Endpoints/0/DisableErrorCertificateIssuerRevocationUnknown = true

Endpoints/1/EndpointURL = opc.tcp://0.0.0.0:4840

Endpoints/1/BindURL = opc.tcp://0.0.0.0:4840

Endpoints/1/SecurityPolicies = SecurityPolicy_None

Endpoints/1/UserTokenPolicies = Anonymous,UserName

Endpoints/1/PKIStore = PKIStore_None

Endpoints/1/TrustAllClientCertificates = false

Endpoints/1/DisableErrorCertificateTimeInvalid = true

Endpoints/1/DisableErrorCertificateIssuerTimeInvalid = true

Endpoints/1/DisableErrorCertificateRevocationUnknown = true

Endpoints/1/DisableErrorCertificateIssuerRevocationUnknown = true

Your Ignition configuration looks fine to me. I've never set up this Schneider software but it also looks fine.

The error your getting is a low level network error. Usually it's either the server just isn't running, or a firewall is blocking your attempt to connect.

We have another Schneider PLC on the network that is communicating perfectly fine. Downloaded and compared configuration files for both systems, not seeing any differences.

I only got it to connect after adding OPC UA Symbol Configuration object.

OPC UA Server Symbols Configuration (schneider-electric.com)

Resolution was reloading firmware on the Scheider device. Not an Iggy issue.