OPC-UA ControlNet - PLC5

I am having issues following the set procedures for connecting a controlnet logix to a plc5. Here is the layout I have in both plc’s and in the opc-ua setup. What am I missing?
Control Logix Setup
0 - Processor
1 - CNB/B
—1 - CNB/B_01_CNET
—2 - 1785 PLC5
—3 - Drive
—4 - 1785 PLC5
2 - 1756 ENBT
—IP xx.xx.xx.103

                 PLC 5 Setup

PLC5/80C
PLC ControlNet Node - 2

DeviceName - Trimmer
Timeout - 30000
Timeout - 30000
Timeout - 30000
Enable Device - checked

HostName - xx.xx.xx.103
Com Timeout - 10000
Cache Timeout - 2400
Connection Path - 1,1,2,1

This isn’t currently supported but will be soon.

Any update on status of this feature?

Should be available in 7.2.4 :slight_smile:

Is this working now in 7.2.4?

You tell me! :laughing:

I saw Tom testing it, so it should be.

Starting with version 7.2.4, connecting to PLC-5 and SLC processors through ControlNet and DH+ are both supported.

In your example above, your connection paths should be:
1,1,2,2 to connect to PLC5 at ControlNet node 2
1,1,2,4 to connect to PLC5 at ControlNet node 4

Connecting to ControlLogix, CompactLogix, PLC-5, SLC and MicroLogix processors using an IP address in the connection path is coming soon.