OPC UA Item Attribute Description

Does anyone know how to get the Description attribute to populate in Ignitions OPC UA server with the tag's description or tooltip value?

I am connecting to Igntions OPC UA server with a 3rd party client app and see that the description field is empty. I would love this attribute to be populated with the Tooltop property in Ignition Tag Editor. (see images)


There's no configuration for this, we're not mapping anything onto the OPC UA Description attribute.

If we did implement this at some point it would likely be the Documentation tag property, not the Tooltip.

Bummer, this would be really helpful for anyone using an external historian or database systems to get a little more context around the items. Appreciate the response. I will throw a suggestion on the ideas board for this.

Unfortunately this is a bigger issue than I originally thought because it prevents me from custom adding descriptions in PI Tags. The Adapter keeps overwriting them because they expect the Description field to be populated.

During my time at AVEVA, I worked the support ticket(s) that led to this KB article being created (or whatever they're called now).

I was just about to write up a rant about how this is a common and very frustrating issue for AVEVA adapter users, but it looks like it may have been fixed in AVEVA Adapter for OPC UA version 1.6.0.296 Allow the PI Point description to | AVEVA™ PI System™ Feedback Portal

Have you tried the new config option in the adapter?

Thanks Cody,
Unfortunately, when I updated to v1.6 of the adapter, AVEVA also updated the OPC UA SDK version to the latest (4.1.0) which created a new issue.
Knowledge

So, it looks like now the ball is back in Inductive’s court to resolve the mismatch of endpoints returned by GetEndpoints and CreateSession.

Additionally, I am getting an error on the OPC UA server certificate:

2025-08-18 16:39:28.608 -05:00 [Debug] OPC UA server certificate with Thumbprint: {ID Number} has invalid domain name specified. The certificate domain name '{IP Address}, 127.0.0.1' doesn't match domain name from the endpoint URL: opc.tcp://{hostname}:62541

I removed the Thumbprint ID, IP Address and hostname for security.
The endpoint is currently configured as…

We've already received a Wireshark capture and punted this back to Aveva. Not sure if that was your ticket or if your capture would look the same. The ticket we received it on was getting the error even with security disabled, so we were able to see it clearly in Wireshark.

You can probably fix this by regenerating the Ignition OPC UA server certificate and making sure to provide the public IP / hostname that external clients see. It's probably not preventing the connection from happening, though.

Ya, I did the wireshark capture and sent into them on a ticket. I did it with security turned off, but still looked encrypted. I added None to the security policies above and then restarted the OPC UA module, so I am not sure why the packets still appeared encrypted. I was still connecting with user/pw.

I don’t think it is security related. The error in the logs says security on Aveva’s end, but they said that is inaccurate and it is the mismatch between the endpoint name and session url? I think it may be related to the URN style paths. They didn’t support that before.

If I regenerate the server certificate, will all OPC UA connections be broken and need new certificate? I am ingesting OPC UA data (Ignition is client) and don’t have a scheduled downtime in production to do this…so maybe I will wait.

The logic their client uses to compare the endpoints from discovery vs the ones returned in the CreateSessionResponse incorrectly includes the certificate as part of the comparison, when it explicitly should not be included: UA Part 4: Services - 5.7.2.2 Parameters.

It's actually a bug in the SDK they use. It's a configurable check in the SDK that they could turn off until it's fixed. It looks like the KB even quotes the SDK docs that mention it.

Yeah, you should wait, then.

Just implemented this, hopefully we can get it into 8.3.1?

@Kevin.Herron Has this made it into a release?

No, even though linking the Description attribute on drag n' drop is easy, it probably won't make it until we also introduce system.opcua.readAttribute (and system.opcua.writeAttribute) scripting functions so that it's possible to read/update descriptions, e.g. with a scheduled script, or some custom trigger that makes sense for your application.

To clarify, my concern isn't consuming OPC UA metadata in Ignition. It's the metadata Ignition publishes as an OPC UA server.

For example, I have Ignition → AVEVA Adapter for OPC UA → PI. The adapter discovers the Ignition tags and synchronizes their metadata. Since the OPC UA Description coming from Ignition is blank, that blank value can propagate into PI and overwrite a manually maintained PI Point description.

I realize AVEVA needs to handle blank metadata more safely, and they have made changes in that area. But I also think there is an opportunity for Ignition to be a richer OPC UA data producer by publishing the metadata that already exists on the Ignition tag.

Ideally that would include:

Ignition Documentation → OPC UA Description
Ignition Engineering Units → OPC UA EngineeringUnits
Ignition engineering limits → OPC UA EURange

EngineeringUnits and EURange are already defined by the OPC UA Data Access information model for analog data, so exposing those would allow OPC UA consumers such as the AVEVA Adapter to automatically build a much more complete representation of an Ignition tag than just its value.

Is this the direction you're considering for Ignition 2027? And regarding Description specifically, should the Documentation mapping you mentioned implementing in August 2025 already be present in current builds?

Ah, sorry, I did not read the history and assumed it was the opposite, which has been asked about often.

The Ignition tag Documentation property has been mapped to OPC UA Description attribute since 8.3.1.

Engineering Units and EURange are trickier because they aren't attributes, they're properties, which means they're actually additional nodes underneath the node in question, and the node in question has to become an OPC UA AnalogItemType node or subclass. This isn't in the cards for 2027.2. I've thought about it a bit, there's some awkward questions about how you configure or decide a tag should be an analog or discrete item type when exposed via Ignition's Exposed Tags; it can't be automatic.

Thanks! That is great news on the description.

Yes, the OPC UA englimits and units is tricky. I would probably follow the OCF model set by OPAS for the implementation, so all vendors start doing it the same way. Since Inductive Partners with COPA I would think they would have some ideas and help this design aspect.