I was previously able to connect to ignition but no longer. I am able to connect to the OPC server using UaExpert. I do get this warning
however I can click ignore and connect.
The settings are the same in UaExpert and Ignition, however ingition shows “connecting” forever and never actually connects. What can I do?
Turn some loggers on to DEBUG and see if we get more information:
com.inductiveautomation.ignition.gateway.opcua.client.ClientManager
org.eclipse.milo.opcua.sdk.client.SessionFsm
https://docs.inductiveautomation.com/display/DOC81/Diagnostics+-+Logs#DiagnosticsLogs-ChangingLoggingLevels
After you’ve set the levels do an edit/save on the OPC UA connection to force a reconnect.
Also - what version of Ignition are you using?
I am currently usingn 8.1.7. Should I go to an earlier version?
As for those log files:
No, 8.1.7 should work just fine.
Can you upload the wrapper logs or logs.idb downloaded from that page?
Looks like it’s failing because the server you’re connecting to stops responding or doesn’t respond quickly enough while we’re browsing DataType information. UaExpert isn’t doing this when it connects.
2021/07/30 08:23:02:269 | WARN | [DataTypeTree ] Browsing failed: BrowseDescription(nodeId=NodeId{ns=0, id=21}, browseDirection=Forward, referenceTypeId=NodeId{ns=0, id=38}, includeSubtypes=false, nodeClassMask=1, resultMask=63)
org.eclipse.milo.opcua.stack.core.UaException: requestId=173 timed out after 60000ms
at org.eclipse.milo.opcua.stack.client.transport.AbstractTransport.lambda$scheduleRequestTimeout$7(AbstractTransport.java:137)
at io.netty.util.HashedWheelTimer$HashedWheelTimeout.expire(HashedWheelTimer.java:672)
at io.netty.util.HashedWheelTimer$HashedWheelBucket.expireTimeouts(HashedWheelTimer.java:747)
at io.netty.util.HashedWheelTimer$Worker.run(HashedWheelTimer.java:472)
If this stopped working recently after upgrading Ignition then it would be worth trying the OPC UA module from the nightly build section, which has some changes that reduce the amount of browsing done on connect. We’ve seen that some servers are simply unable to handle it…
I had an older version installed and for some reason had to remove ignition a while back. I installed whatever the latest version was yesterday, so that could be it
I reverted back to version 8.4 and that resolved the issue.
Hey, my system behaves the same. I only have the additional warning:
[16] Initialization failed: OpcUaSession{sessionId=NodeId{ns=1, id=3edfa222-b17d-4c21-9fa4-dcae2aa5997e}, sessionName=ignition[POD-1-GW]_pac-scs-plc_1728632414817}
I did not change my Ignition Version (8.1.35), but the OPC Server version (SimaticNet V19 Update 2). I needed to update to this version, but now the OPC-UA client fails with the behavior described above.
Does somebody has any idea how to handle this? Is there any settings to say Ignition to wait longer? I tried to play around with the settings, but nothing changed.
Unfortunately it is quite urged, since I am on commissioning right now..
The thing is, that I have the same project running on an other Network and there it works fine.
Solved it.
I guess this is a very specific problem, but if somebody is interested and uses SimatciNet:
I had tracing enabled, which slows down the communication. When I disabled this, the connection was successfully established.