Im trying to use the parameter {Recipe} to fit it in a filepath
the filepath is {[.]../TCP SLOW PSI GP1/Query[0,2]
but no matter what i try it doesnt like the syntax
is it even allowed?
Here are some of the attempts
{[.]../+{Recipe}+GP1/Query[0,2]}
{[.]../+"{Recipe}"+GP1/Query[0,2]}
"{[.]../"+"{Recipe}"+"GP1/Query[0,2]}"
"{[.]../" "{Recipe}" "GP1/Query[0,2]}"
lrose
November 20, 2022, 3:14am
2
You can not have nested {} in an expression.
Officially you can use the tag() expression to accomplish this. it isn’t always the best approach however.
tag("{[.]../"+{Recipe}+"GP1/Query[0,2]}")
Where are you attempting to do this, there may be a better way?
it is in an expression tag , trying to make a tag that takes a single row out of the 2nd column out of a bunch of different tables and it changes depending on a recipe name , then it adds them all together and divides by the amount of tables to get an average
any chance this works for getting the 2 to be a parameter as well?
tag("{[.]../"+{Recipe}+"GP1/Query[0,{column}]}") something like this?
lrose
November 20, 2022, 4:34am
4
Where are the parameters coming from?
In theory I think you would want something like:
tag("[.]../"+{Recipe}+"GP1/Query")[0][{column}]
The tag() expression takes a string tag path, so you’re building that string.
the parameters are coming from a UDT , they are recipe , profile number , and now column if i can get that to work , ill have to test it on monday
after a bit of tries i got it to work thank you
it ended up being
(Tag("[.]../"+{Recipe}+" "+"GP1/Query[0,2]")
i was forgetting to add a + " " + in between for a spacer