I think it would be nice if we could configure a redundant device for devices. If the gateway detected a connection failure it would get data from the secondary device. I would like some timeout settings and perhaps a sticky/auto return to master. Also a hot/cold setting for the secondary device.
BTW how do you guys keep up with soooo many feature requests?? It seems daunting
The way we do this is by having 3 devices. PLC1A, PLC1B, and PLC1Master. All our tags point to PLC1Master. I have a gateway script that runs and checks the connection status to PLC1A and B. If there is a fault I use the IA Labs scripting module to change the IP address of PLC1Master to the IP of the still available PLC (A or B).
I’m wondering what you use to check connection status…
Using the IA Scripting module you can change the host name like so:
system.device.setDeviceHostname(‘PLC1Master’, ‘112.112.112.14’)