Hello everyone,
I am trying to connect my PLC to Ignition, but I get the error message below. My Ignition Designer is in a VM, and I can ping the PLC IP address from that VM. Does anyone have information on how to resolve this? Thank you!
The gateway makes the connection to the PLC, not the designer.
Can you ping from the gateway to the PLC?
What firmware is in the PLC? (If >20, you are using the wrong driver.)
You are correct I was using the wrong driver, thank you for your help!
Hi,
I am facing the same kind of issue.
Connecting : Protocol: EIP - Run Mode.
Could you please help me understand what this means and suggest a solution?
This is a question about your logix version. What version of RSLogix and/or Studio are you using? Depending on this, you will want to change which driver version you apply. Rockwell changed their driver interface around the 20/21 version split.
I'm currently using studio 5000 V32.01
And my plc is 5380 compact logix (5069-L330ER)
Ok I'll check and let you know