Potentially unexpected redundancy behavior?
Using 8.1.25.
I have two servers in redundancy that host a vision application. Had unexpected behavior last time they had to patch the primary server so just wanted to clarify a few things.
When I manually failover, it lasts until I fail things back over and I see on the status page the status change from Backup to Master or vice versa.
  1. However when server 1 was given a hard reset to run its updates without being failed over first - on server 2 the status page never changed so it didn’t seem clear that server 2 took over although vision users did increase and the instance of the applicaiton I had seemed to fail over ok. Normal to not see the status change in this event?
  2. Also, when server 1 came back online, it resumed status as the master which I was not expecting - is this expected behavior?
  3. A general question to people who do use it, does the redundancy not work nicely with the master getting a hard shut off, I know its better to gracefully failover when you can but has anyone experienced issues from unexpected failovers?
  1. This could be related to the Backup Node Settings (if Ping Max Missed is a high value and/or the Ping Timeout is high).
  2. This depends on the Master Node Settings (Automatic or Manual).
  3. I specifically recall issues between 8.1.18-8.1.24 with a redundant install I was working on. 8.1.25 introduced a proper fixed that allowed redundant pairs to be on different versions for the sake of upgrading. Since, then I’ve not any issues like that.
8.1.25 snippet: