Power Chart Y axis with fixed range (auto = False) still rescales to visible data (Ignition 8.3)
The Power Chart is configured entirely from a script. For each pen, an axis with a fixed range is created. The low/high limits come either from a configuration table or from the tag’s EngLow/EngHigh properties. Before building, props.axes and props.pens are reset to []. The pen’s axis is set to the same name as the axis.
Take a trend with a fixed Y axis range of -1 to 10. When we open it on the last 24 hours, the axis shows -1 to 10 as expected, since the tag has been at -1 all day. But when the tag value is 9 and we switch the chart to realtime with a window of the last minute, so that only the value 9 is visible, the Y axis changes to roughly 8.9 to 10. If the visible window also contains lower values, for example 24 hours with both 0 and 9 in view, the axis stays at -1 to 10. So the fixed range only seems to be ignored when all the visible data is near the top of the range.
I already tried converting min and max to float, hardcoding 'min': -1.0, 'max': 10.0, and switching interaction.mode from panAndZoom to xTrace. None of these changed the behavior. The 8.3 documentation lists only auto, min and max under axes[].range, so i don't think a property is missing.
Is this expected behavior or a bug? And is there a way to keep the Y axis truly fixed, regardless of the visible data?
Are you sure the pen's axis is really set to the axis you want ?
Just tested this out on 8.3.9 and it works if I configure it this way:
I tested this out with a sample tag that represents the number of seconds, and in realtime I'm watching the last 10 seconds.
The chart does show me ONLY the range from 0 to 10.
EDIT : Oh actually you might be right. To be sure I was in the same conditions as you were, I put my min to -1 and it did start to behave completely differently....
Apparently it is truly a bug when your min is a negative value ?
EDIT 2: Actually even weirder, if I put -2 as my min, it does work correctly again. Maybe a bug ONLY with min = -1 ?
Thanks a lot for testing this, and for taking the time to reproduce it. That is very helpful. We can confirm the same: with a min of exactly -1 the axis starts rescaling to the visible data, while other values behave correctly. We changed our min from -1 to -1.1 as a workaround, and the axis now stays fixed and displays as -2 on the chart, so that works for us until this is fixed.
Please open a support ticket and report this bug. (This forum is not the official place to report bugs.)