Now i have a litttle problem. We collect machine datas about ignition. But if the machine is switched off, we get always the last values. In designer it shows “Uncertain, showing last value”.
But we don’t need it. And i don’t find any solution to switch off that.
Tanks for answer. Sorry I think myy explaination was inexact. The main problem is, we use igntion also for data transport to other systems.
If the maschine is switch off, we get always the last values.
For example this picures. On is the state from ignition (designer)… And the other are the values in our subprogram.
The machine is not running.
No, but every tag read delivers both value and quality. Inspect the quality in your scripting/expressions and substitute whatever you want to show when the quality code indicates your machine is disconnected.
“No”… ok, thanks.
Thats was it what i want to know. I asked because in other OPC programms you have the possibility.
I thought i can solve it without a script for each tag.