Problem reading Float Value from Modbus TCP

Hello:
I’ve a Modbus TCP slave which communicates with Ignition SCADA. I am trying to read float values from holding register 10102. The value is read correctly on the gateway tags. I would like to read the float value in my designer project. So, I created a OPC tag with data type float and mapped it to HR10102. But I am receiving some integer value instead of float. Could you please let me know what could be the problem?

Thank you very much in advance,
Shwetha.

Step 1. Read the manual. https://docs.inductiveautomation.com:8443/display/DOC79/Modbus+Addressing

You need to have your address as HRF10102, and set the data type to float.

Thank you!. That solved the issue