I created Alarm status table and I am getting alarm from sample program. I think that tags are from ignition simulator. I already deleted sample project, clear simulator tags and delete sample device. Does someone have solution how I can remove this alarm? I would like to have only alarms from my program not from predefine ignition sample program.
Use the 'Source Filter' property on the Alarm Status Table...
or 'Provider Filter' or 'Display Path Filter'...
Alarm Status Table filtering
Živijo.
Hvala za odgovor. Ta filtracija mi bo prišla prav v prihodnje, sem pa iz te slike našel rešitev.
V Tag Browser sem pogledal vse tage iz vseh virov in so bili v njem Tagi od demo projekta. Zakaj so bili sploh tam pa ne vem ker je to ÄŤisto loÄŤen projekt.
V glavnem sem še tisto izbrisal in sedaj dela.
Lep pozdrav.
Tags don’t belong to projects, they exist on the Gateway entirely independent of them.
They 'belong' to the Tag provider.
You can have many Tag providers and many tags in them, and they will be accessible from all projects on the Gateway.
You can also choose in the 'Project Properties', which Tag Provider is the Default for that project.