First off, we should probably make sure that it’s not a problem with one of the pipeline blocks. Can you maybe post a screen shot of the Status>Alarm Pipelines screen when it happens? What is the final state that it sits in?
Some way to clear the pipeline would be good, and should probably show up on that screen if you’re logged in. When you save the pipeline, the previously running version gets retired, but I don’t think that that drops the existing events out…
Finally, for what it’s worth, there actually is a built in limit to prevent infinite loops- alarm events can only transition between block 1024 times (although should anyone ever need more than that, it’s possible to reset the counter through the Set Property block)
I have the same problem:
On Notification active pipeline it work ! but on Clear pipeline it doesn’t work.
A function to purge would be cool
Thanks thread-dump.txt (37.5 KB)
I’m still have a problem with “stuck” tags in the alarm pipeline. I’m running Ver. 7.9.5 and was working with support by email for over 4 months. The problem is still in my project! I have emailed over 3 weeks ago about this and no one has reply this last time. Any suggestion? My project has one data type tag and 255 data type instance tags of it, totaling about 610 tags per data type instance. Plus about 150 regular tags. About 25% are alarm tags and 30% are history tags. So the grand total of tags is roughly 155,000 tags and I wonder if I need to do some kind of data type instance tag scan to make sure all of the data from my data type instance is correct in my instances. Any suggestion because I stuck know!