Reading ASCII from a Click PLC

Hello, I'm trying to read a part number containing numbers and letters from a Click PLC. I scan the number into the HMI, which stores the 12-character string into 12 TXT registers in the click. Trying to figure out how to retrieve them, in proper order, as a single entry in Perspective. I have modbus addresses for each register, but I'm lost. I do this succesfully with ascii strings from Allen Bradley PLC's, but the Click does not have ascii.

More of a PLC guy than a code, guy, so help would be appreciated.

Modbus addresses in PLC.

What the tags look like. Not understanding this.

Can you show a screenshot of your current tag(s)? What values are they displaying and what's the datatype? And what does your ultimate destination look like?

As @PGriffith mentioned, include a screenshot of your setup for the best help, but what you are looking for is string addressing in the manual.
Modbus Addressing | Ignition User Manual

Specifically, this part

The device connection also has some string handling (advanced) options that will need to be considered

1 Like

Updated.

Try this in a single OPC tag

[yourDeviceName]1.HRS36865:12
  • [yourDeviceName] tells Ignition which configured device to use
  • 1 is the modbus unit Id
  • HRS means holding register with string-type value
  • 36865 is the starting address
  • :12 means read 12 characters from contiguous memory locations starting from above
1 Like

Brilliant, thank you. That worked perfectly! Really apprreciate it!