Redudancy with docker, client connection to backup gateway
Good morning
I have a problem:
Version ignition 8.1.14
Windows 10 Pro 21H1
Docker desktop version version 4.5.0 (74594)
I’m doing a redundancy test with 2 docker instances as an attached schema.
Redundancy is correctly connected between the 2 servers within the docker network via ip 172.19.0.x
The client is on the host machine and connects to the master gateway via exposed port 9088 on ip 10.5.90.253.
I connect correctly from the browser both to the master gateway on port 9088 and to backup on port 9188.
In the client launcher configuration I insert the master IP, but the address of the “gateway.redundancy” within the configuration automatically takes the IP configured as a backup on the redundancy settings (ie 172.16.0.3).
Going to modify the parameter in C: \ Users \ User \ .ignition \ clientlauncher-datavision-client-launcher.json by inserting the correct backup address http://localhost:9188 instead of 172.19.0.3:8088 (that is internal docker) , and starting the project, the client always points to 172.19.0.3.
The question is:
Is it possible to make the client point to a different backup gateway than the one set up in the redundant gateway?
You can set a Public HTTP address that will be delivered to clients and designers for both servers:
https://docs.inductiveautomation.com/display/DOC81/Web+Server+Settings#WebServerSettings-PublicHTTPAddresssettings
Hi, thanks for reply.
I need to setting in both master and server gateway
master
public address :localhost
public port : 9088
backup
public port : 9188
Correct?
Ok i will put instead localhost, ip 10.5.90.253 and work thanks