Hi all,
I have a Data Types with 6 tags all of them related with an alarm with mail notification (It sends a mail if the value stay under treshold for more than 2 hours).
It works fine, but one of this alarm stay High for a lot of days and I need to send a reminder to users every 24 hours (if the alarm is always high obviously).
It deals with a filter in a circuit (so physically, if you don’t clean the filter, the alarm can’t go low).
I can I set this condition?
Thank you
You can setup a separate alarm pipeline for this type of alarm. Have a look at this page.
1 Like
Yes, those settings would be the same. Those tell ignition when the alarm should be active. The pipeline is what tells ignition to do about an active alarm.