Retrieve acknowledgement notes
I’ll use
system.alarm.acknowledge
to acknowledge alarms with notes.
but I’ll use
system.alarm.queryStatus
to retrieve alarm status
but, I don’t find any acknowledgement notes.
How should I correctly retrieve the acknowledgement notes?
System.alarm.queryStatus will return a list of AlarmEvent objects
You can call getNotes on those AlarmEvent objects:
https://docs.inductiveautomation.com/display/DOC79/Alarm+Event+Properties+Reference#AlarmEventPropertiesReference-TheAlarmEventObject
thank you, ethomason!!
Hi;
I used getNotes() in the following code but it returns blank. But, when I check the Ignition Alarm Status Table created in a GUI, it shows the notes.
alarms = system.alarm.queryStatus(State=["ActiveUnacked","ActiveAcked","ClearAcked","ClearUnacked"], includeShelved="false")
logger.info(str(type(alarms[0])))
# <type 'com.inductiveautomation.ignition.common.alarming.BasicAlarmEvent'>
logger.info(str(type(alarms[0].getNotes())))
# <type 'unicode'>
logger.info(str(len(str(alarms[0].getNotes()))))
# len: 0
What could be wrong?
You are only looking at one alarm event. What happens when you loop through the entire dataset?
There was only one alarm in the set. And, it comes from an Inductive Automation server that I have set up for development. It only has one tag. And, then I put it into alarm. I actually had a loop that would iterate through the alarms object in general. But, I took it out to make the troubleshooting easier. What do you think I should do?
I should add that I compared the UUID of the alarm from queryStatus with the UUID of the alarm that appears in the Alarm Status Table created using designer. The UUID was the same for both of them.
Can you remote into the machine to help me out?
Hi Adolfo, if you need immediate assistance I recommend getting in contact with support.
Solution Named Query :
SELECT a.id, a.displaypath, a.eventtime, b.notes, b.user
FROM alarm_events a
LEFT JOIN (SELECT TAB_1.id, TAB_1.notes, TAB_2.user FROM
(SELECT id,
strvalue as ‘notes’
FROM alarm_event_data
WHERE propname = ‘ackNotes’) AS TAB_1,
(SELECT id
,strvalue as ‘user’
WHERE propname = ‘ackUser’) AS TAB_2
WHERE TAB_1.id = TAB_2.id) AS b
ON a.id = b.id
WHERE b.notes IS NOT NULL
ORDER BY a.eventtime DESC