I’m looking for how to retrieve the tag path of the UDT definition to which a tag belongs to, within an instance of the UDT.
I’m sure I’ve done this before but having a mental blank…
For example, I want to return ‘Packaging/Filtration/Devices/Filler’ from below, given the tagPath for the ‘Filtration Status’ tag.
I’m assuming you are in Ignition v7.9.x, but you might be able to do something like this:
tagPath = "[default]Path/To/Tag/Line 2/Filler.typeId"
typeId = system.tag.read(tagPath).value
print typeId
I don’t have 7.9 on-hand to test that out, but I am curious as to the solution.
I found that in Ignition 8.0, this seemed to work:
tags = system.tag.getConfiguration(tagPath)
for tag in tags:
tagType = tag['tagType']
if str(tagType) == 'UdtInstance':
typeId = str(tag['typeId'])
print typeId
Cheers,
Roger
Thanks for the prompt! You can get the typeId in 7.9.14 from browseConfiguration.
Function to get the UDT definition tag path below:
def getUDTTagPath(tagPath, recursion=0, sRet=None):
# if we recurse more than 20 times, kill it!
if recursion > 20: raise NameError("Too many recursive calls made!")
# get the parent folder name and its configuration, so that we can check if the tag we passed in is a UDT_INST
parentTagPath = "/".join(tagPath.split("/")[0:-1])
tagName = tagPath.split('/')[-1]
tagsConfig = system.tag.browseConfiguration(parentTagPath, 0)
for tagConfig in tagsConfig:
cfgTagName = tagConfig.getName()
if cfgTagName == tagName:
tagType = tagConfig.getTagType()
if str(tagType) == 'UDT_INST':
for prop in tagConfig.getProperties():
if str(prop) == 'typeId':
# we found the UDT definition tag path, return it
sRet = tagConfig.get(prop)
return sRet
else:
# the current tag element is not a UDT_INST, so try the parent
sRet = getUDTTagPath(parentTagPath, recursion+1, sRet)