S7-300 Connection to Ignition

I have an S7 315-2 PN/DP with aditional CP343-1 Lean. I am trying to connect the plc to ignition with s7-300 driver over the lean cp card.

So the problem i have is when i connect ignition i cant get online with a PG, and when i am online with PG icant connect with ignition.

The connection resurces on the PLC are set to 5-OP 5-PG 2-S7 BASIC . I tried modifing these ressureces but still no luck. Any ideas ? Maybe a problem because of the cp lean card ?

How many of the connection resources are in use already?
Normally you can check this with a web browser on a 300 series unit.

1 Like

So to update the situation. The CP343-1 Lean apparently supports only up to 5 connections. I had more on that cp lean and thats why it did not connect

2 Likes