Script will not change tag value PLC to PLC. I know I have write enabled in PLCs and in gateway
Define the source and destination tag paths
source_tag_path = "[default]Line1/Data/L1_RoboticStacker/Ignition_Retract"
destination_tag_path = "[default]Line1/Data/L1_RoboticStacker/trg1"
Get the tag values
source_tag_value = system.tag.read(source_tag_path).value
Write the value to the destination tag
system.tag.write(destination_tag_path, source_tag_value)
I'll assume that this is for Ignition V8.1, and so you should be using the read* and write* functions as the ones that you have posted are deprecated.
That being said, everything that you show here should be correct "technically". This would indicate to me that something in the device is writing over your write or you have some other type of race condition. You should only ever write to a tag (PLC or Ignition) from one direction, doing otherwise will cause issues.
    source_tag_path = ['[default]Line1/Data/L1_RoboticStacker/Ignition_Retract']
    destination_tag_path = ['[default]Line1/Data/L1_RoboticStacker/trg1']
    source_tag_value = system.tag.readBlocking(source_tag_path)[0].value
    system.tag.writeAsync(destination_tag_path, [source_tag_value])
Also, please use the preformatted text option to post code, makes it a lot easier to help and read your code.
Levi, please read Wiki - how to post code on this forum.
Then please use the pencil link below your post to edit and fix it.
Thanks.