Following is the address definition for delta plc
Prefix : Y
Start : 0
End : 12
Step : None
Unit id : 1
Modbus Type : Coil
Modbus address : 1281
It was showing bad tags so checked the command passed to modbus.
Ignition is generating following command
000A00000006010105000310
First six Message id : 000A00000006
Unit id : 01
Function code : 01
Start Address : 0500 = 1280 Decimal
Number of Address : 0310 = 784 Decimal
Even though number of address configured is 12 so message should get 0C00 instead of 0310.
Please help. Thanks in adavance.