If you have 10 tags at the Edge node it's going to transmit all 10 tags even if you're only "interested" in seeing e.g. 3 of them.
Then on the server, the only way to get the tags into a tag provider is to use a reference tag, as you can't put history on the MQTT folder tags as they disappear and recreate with rebirth,
Sorry if I haven't understood your situation fully, if so please elaborate.
Thanks for the response, I'll provide more specific context.
This is as a means to provide OT data to IT so they can leverage near real time manufacturing data in their reports.
The path way is "Tag provider Gateway" > "IIOT Gateway" > "Azure DataWarehouse"
The tag provider gateway is for our full SCADA so has every tag available (Several thousand), the plan is to use the Cirrus Link MQTT Azure injector to send the data to the Datawarehouse... problem is this is charged based on the number of messages, so IT only want to "subscribe" to information as and when they have the need to. If we sent the whole tag provider this would flood them.
Given how our tag providers are structured there would be little benefit using the sub folders as the target as this would still give them many more than they need.
This very well could be the wrong way to go about this. I'm open to alternatives.
You aren't wrong. I proposed a feature change to Cirrus Link for similar applications. No commitment or timeline at this time. The folder tree of reference tags is the current best approach to sending a subset.
Yeah, I would love the ability to be able to set a tag prop or something that would trigger it to be added to the list of "MQTT" tags and not have to do the reference tag folder trick.
If I understand the request correctly, I think you can do this by adding a ExcludeFromPayload custom tag property to the tags you do not want included in the MQTT transmission.
The warning that applying the flag to multiple tags will "result in significant system performance issues" is not inspiring.
I also agree that the inverse of only transmit if the flag is present would be preferable.
Any thoughts on other ways to approach this? I was considering logging directly to the azure data warehouse with the historian but run into a similar issue where we have used the splitter so this would be a third target.
You do have the option to publish a custom payload using scripting functions. Though, I'm not sure that's any more desirable than a folder of reference tags.
I believe the warning is only about the TagEventTracer custom property and not the ExcludeFromPayload prop. So system performance should not be an issue.
Have you considered creating a batch for your tags, instead of sending mqtt messages every second or time the tags update, send them every 1, 5 or 15 minutes with all corresponding data.
I've only experimented a bit with the Transmitter module. How do you batch the updates together? And if there were multiple tag changes in that window, does it send them all, or just the current value?