Sequence Number Error from OPC server

I didn’t see much along the lines of these errors on the forum that pointed to a relevant cause. Does anyone have any ideas on what may be causing these intermittent errors? They aren’t too often, but they are scattered throughout the logs and I wanted to try and address them.

What version of Ignition is this happening on?

8.0.2 Release ( 8.0.2 (b2019060511))

Okay, I think this might be fixed in 8.0.3, which includes a newer version of the OPC UA SDK that has a fix for a bug that looks a lot like this.

In the meantime, you don’t need to worry too much because the ResendData call is succeeding and you aren’t losing any realtime values.

1 Like

Ok thanks. I’ll update the system once the 8.0.3 release comes out and see what happens