Hi all, I would like to ask, how do I configure alarms in Ignition and display it in the Alert Status Table from one of the Templates ?
I tried configuring the tag but nothing pop ups
- The first image is the settings for the an alert:
If Ignition is unable to get new values from the database query, like no change in values for the past 3 seconds, an alert should be on to notify user to check the temperature sensor connection.
I tried using Bad Quality since it can work for no connection to database.
- The second image is the settings for another alert:
Ignition read values from the database and calculate the mean and find the maximum value of the values it reads,if the values differs by 10, the alert should be on to notify the user that they should check the screen
Sample Code for Temperature varying too much from a reading by 10 from database
history = np.zeros([32, 32, 5], 'f')
idx = 0
movavgmax = np.zeros((5,1), 'f')
movavgmin = np.zeros((5,1), 'f')
hyst = 0.8;
## Simulate value inputs into the Tag using raw data
rawdata = [2977, 2988, 2966, 2995, 2966, 2973, 3002, 2975, 2983, 2987, 2973, 2984, 2980, 2961, 2966, 2984, 2945, 2952, 2955, 2951, 2943, 2968, 2950, 2945, 2945, 2976, 3006, 2946, 3006, 2918, 2982, 2962, 2926, 2987, 2962, 3009, 2972, 2973, 3002, 2977, 2976, 2997, 2991, 3002, 2972, 3000, 2968, 2982, 2986, 2964, 2944, 2947, 2962, 2955, 2929, 2944, 2944, 2931, 2978, 2962, 2930, 2943, 2927, 3001, 2952, 2983, 2974, 2965, 2989, 2966, 2951, 2975, 2992, 2986, 2955, 2945, 2955, 2978, 2969, 2995, 2972, 2997, 2948, 2950, 2932, 2951, 2946, 2935, 2969, 2941, 2944, 2953, 2934, 2951, 2959, 2946, 2963, 2970, 2981, 2976, 2989, 2993, 2954, 2978, 2983, 2983, 2982, 2975, 2992, 2973, 2977, 2969, 2979, 2966, 2959, 2955, 2923, 2933, 2938, 2953, 2949, 2940, 2948, 2945, 2906, 2973, 2954, 2988, 2958, 2971, 2991, 2959, 2956, 2950, 2983, 2958, 2957, 2980, 2960, 2975, 2979, 2973, 2976, 2986, 2992, 2981, 2984, 2965, 2942, 2935, 2907, 2929, 2939, 2931, 2955, 2963, 2937, 2957, 2986, 2969, 2996, 2960, 2963, 2998, 2958, 2969, 2984, 2955, 2966, 2974, 2967, 2959, 2958, 2993, 2990, 3004, 2994, 3009, 2998, 2998, 2945, 2932, 2933, 2935, 2901, 2925, 2914, 2946, 2926, 2994, 3023, 3009, 2972, 2957, 2961, 2944, 2979, 2975, 2969, 2939, 2996, 2973, 2961, 2935, 2987, 2966, 2993, 3025, 3008, 3028, 3010, 2990, 2960, 2944, 2952, 2903, 2926, 2921, 2935, 2921, 2932, 2936, 2967, 2932, 2963, 2991, 2980, 2966, 2973, 2986, 2978, 2966, 2969, 2973, 2955, 2955, 2962, 2981, 3015, 3018, 3017, 3017, 2992, 2962, 2966, 2930, 2933, 2932, 2909, 2911, 2922, 2944, 2904, 2914, 2934, 2984, 2977, 2967, 2996, 2978, 2985, 2996, 2987, 2966, 2965, 2972, 2966, 2975, 2979, 2975, 3003, 3005, 3002, 2985, 2979, 2965, 2952, 2955, 2925, 2912, 2922, 2913, 2934, 2917, 2933, 2927, 2909, 2931, 2978, 2946, 2973, 2988, 2968, 2976, 2989, 2968, 2958, 2949, 2961, 2966, 2965, 2959, 2975, 2986, 2980, 2954, 2942, 2964, 2941, 2916, 2903, 2897, 2911, 2893, 2916, 2880, 2910, 2926, 2923, 2961, 2969, 2976, 2974, 2991, 3010, 3022, 3004, 2963, 2966, 2964, 2949, 2944, 2956, 2956, 2942, 2954, 2946, 2955, 2948, 2930, 2941, 2925, 2923, 2895, 2909, 2894, 2870, 2905, 2888, 2917, 2903, 2917, 2960, 2975, 3014, 3027, 3031, 3011, 3008, 2971, 2959, 2958, 2945, 2946, 2948, 2944, 2945, 2936, 2935, 2924, 2918, 2937, 2938, 2917, 2900, 2893, 2892, 2895, 2873, 2910, 2884, 2910, 2918, 2932, 2974, 2975, 2997, 3021, 3043, 3015, 2998, 2966, 2953, 2952, 2941, 2946, 2966, 2936, 2947, 2935, 2942, 2937, 2926, 2936, 2916, 2934, 2909, 2893, 2874, 2881, 2896, 2893, 2918, 2903, 2927, 2920, 2985, 2941, 2982, 3003, 3001, 2990, 2991, 2957, 2964, 2954, 2948, 2956, 2953, 2939, 2925, 2933, 2923, 2936, 2928, 2935, 2926, 2929, 2903, 2885, 2891, 2877, 2916, 2888, 2894, 2916, 2957, 2956, 2985, 2970, 2984, 2971, 2971, 2981, 2968, 2953, 2950, 2952, 2934, 2930, 2933, 2940, 2947, 2938, 2927, 2933, 2918, 2927, 2924, 2924, 2925, 2909, 2897, 2913, 2899, 2910, 2925, 2918, 2911, 2896, 2985, 2966, 2968, 2975, 2973, 2958, 2962, 2962, 2960, 2949, 2949, 2952, 2940, 2932, 2946, 2941, 2932, 2931, 2931, 2926, 2932, 2940, 2928, 2919, 2917, 2923, 2910, 2927, 2915, 2927, 2937, 2935, 2973, 2966, 2952, 2980, 2961, 2958, 2963, 2971, 2938, 2965, 2956, 2950, 2949, 2940, 2947, 2951, 2940, 2939, 2938, 2930, 2941, 2926, 2923, 2913, 2921, 2914, 2927, 2918, 2955, 2946, 2944, 2922, 2976, 2971, 2964, 2956, 2945, 2945, 2942, 2956, 2959, 2953, 2950, 2948, 2943, 2936, 2952, 2944, 2943, 2941, 2945, 2943, 2936, 2930, 2935, 2931, 2924, 2918, 2907, 2927, 2943, 2948, 2959, 2934, 2965, 2963, 2950, 2971, 2960, 2953, 2944, 2948, 2938, 2936, 2958, 2944, 2958, 2954, 2935, 2940, 2939, 2943, 2942, 2941, 2944, 2932, 2943, 2932, 2931, 2940, 2927, 2938, 2946, 2951, 2935, 2956, 2968, 2961, 2949, 2962, 2974, 2977, 2959, 2965, 2943, 2955, 2952, 2956, 2955, 2947, 2953, 2935, 2936, 2954, 2948, 2953, 2941, 2942, 2940, 2939, 2933, 2929, 2912, 2919, 2923, 2940, 2948, 2968, 2974, 2950, 2962, 2951, 2965, 2966, 2947, 2962, 2938, 2956, 2951, 2961, 2956, 2944, 2955, 2949, 2943, 2951, 2949, 2952, 2942, 2931, 2942, 2938, 2960, 2947, 2935, 2932, 2926, 2934, 2921, 2935, 2947, 2949, 2954, 2964, 2951, 2949, 2946, 2963, 2948, 2958, 2957, 2962, 2955, 2941, 2967, 2949, 2937, 2952, 2953, 2961, 2956, 2930, 2966, 2928, 2946, 2929, 2929, 2939, 2946, 2959, 2954, 2930, 2949, 2950, 2965, 2991, 2948, 2961, 2965, 2962, 2933, 2962, 2976, 2935, 2946, 2948, 2954, 2965, 2950, 2949, 2953, 2965, 2946, 2937, 2947, 2943, 2942, 2936, 2946, 2942, 2944, 2922, 2942, 2912, 2969, 2963, 2928, 2950, 2963, 2969, 2953, 2971, 2946, 2948, 2955, 2957, 2951, 2937, 2945, 2945, 2954, 2937, 2969, 2962, 2961, 2943, 2942, 2944, 2945, 2937, 2945, 2939, 2953, 2946, 2926, 2988, 2929, 2957, 2976, 2938, 2960, 2983, 2969, 2959, 2953, 2971, 2932, 2966, 2934, 2950, 2959, 2948, 2970, 2942, 2941, 2954, 2942, 2944, 2952, 2952, 2946, 2929, 2937, 2944, 2960, 2943, 2951, 2961, 2941, 2947, 2949, 2936, 2956, 2919, 2974, 2956, 2953, 2949, 2969, 2954, 2952, 2939, 2964, 2962, 2962, 2960, 2957, 2956, 2961, 2940, 2949, 2940, 2958, 2946, 2949, 2921, 2974, 2957, 2958, 2955, 2954, 2934, 2970, 2939, 2952, 2948, 2964, 2947, 2921, 2935, 2965, 2952, 2954, 2949, 2939, 2955, 2938, 2966, 2960, 2936, 2942, 2949, 2953, 2943, 2960, 2950, 2962, 2944, 2936, 2931, 2960, 2976, 2919, 2945, 2918, 2935, 2947, 2952, 2963, 2947, 2954, 2962, 2936, 2950, 2960, 2944, 2956, 2941, 2959, 2965, 2953, 2965, 2953, 2936, 2952, 2940, 2947, 2959, 2946, 2935, 2978, 2950, 2966, 2991, 2917, 2891, 2949, 2938, 2961, 2969, 2942, 2970, 2963, 2964, 2956, 2952, 2949, 2963, 2947, 2951, 2950, 2948, 2969, 2968, 2939, 2941, 2949, 2939, 2974, 2981, 2949, 2920, 2972, 2949, 2973, 2944, 2921, 2954, 2895, 2912, 2979, 2937, 2973, 2956, 2964, 2961, 2957, 2946, 2940, 2938, 2975, 2959, 2952, 2955, 2987, 2970, 2960, 2939, 2957, 2937, 2972, 2925, 2947, 2983, 2961, 2987, 2940, 2909, 2953, 3001, 2955, 2987, 2966, 2953, 2956, 2946, 2894, 2938, 2935, 2966, 2940, 2958, 2964, 2958, 2949, 2951, 2957, 2966, 2950, 2972, 2948, 2970, 2983, 2948, 2972, 2976, 2925, 2962, 2970, 2871, 2970, 3023, 2935, 2976, 2971, 2948, 2937, 2966, 2931, 2943, 2950, 2941, 2934, 2977, 2939, 2937, 2978, 2940, 2980, 2979, 2953, 2958, 2939, 2949, 2955, 2925, 2948, 2951, 2913, 2912, 2935, 2987]
rawdata = np.array(rawdata)
rawdata = np.resize(rawdata,(32,32))
rawdata = (rawdata/10.0)-273.15
rawdata = {[.]Row0.value}
import math
pyData = system.dataset.toPyDataSet(value)
import jnumeric.PyMultiarray as np
alarm=0
avg = np.resize(rawdata,(1024,1))
avgs = [sum(vals)/len(avg) for vals in zip(*avg)]
Max = 0
Max=(max(avg))
if ( Max - avgs >= 10.0):
alarm=1
else:
alarm=0
return (alarm)
Maybe I should setup another script tag to read data from database and process the value difference then compare it with the setpoint for this… but I wonder if it’s possible with a query tag