Siemens enhanced driver with Tia portal V20 Firmware 4.0

Hi,

Does someone got the Siemens driver working with a PLC on firmware V4 and Tia V20?
Before upgrading firmware from V3 to V4 and from Tia V18 to V20 was the communication working.

How i get in the log that a password i required

DEBUG

SymbolicAddressSpace

08Jan2026 10:07:36

Failed to load symbols

DEBUG

SymbolicAddressSpace

08Jan2026 10:07:36

Failed to load symbols. Error: 'AGL40_SYMBOLIC_PASSWORD_REQUIRED', '0xFFFA010C' SError: 'AGL40_SUCCESS','0x0'

DEBUG

SymbolFsm

08Jan2026 10:07:36

S(LOADING)               x E(LoadSymbolsFailure[cause=de.deltalogic.accon.aglink4.AglIOException: Method: 'symbolic_LoadAGLinkSymbolsFromPLC', Error Code: 'AGL40_SYMBOLIC_PASSWORD_REQUIRED', Error Nr: '0xFFFA010C', Error Message: 'AGL40_SYMBOLIC_PASSWORD_REQUIRED',]) = S'(LOADING_WAIT)        

DEBUG

SiemensS7Client

08Jan2026 10:07:36

This connection requires a password for symbolic access.

DEBUG

SiemensS7Client

08Jan2026 10:07:36

Error occurred while setting password for the PLC connection.

From what i see in Tia Portal configuration the password is the same as previously.
Here the setting in Ignition

Which v4 firmware are you on? I know there were some earlier ones that were buggy for the upstream connections.

V4.0.0 and Ignition 8.3.2 (In docker)

Given the issues, I would suggest v4.0.4 and see if that helps. If anything, it might get you away from other bugs that have popped up in that firmware.

Well update to 4.0.4 didn’t help, i will need to check it on a fresh software if it works or not.