Hello,

I hope you are well !

I would just like to declare the OPC Item Path in a tag coming from a Siemens.

Example:

Name of my device: API Puisard
Data Siemens Adress: DB21.DBD16 (its a Udint, so I try in Ignition with INT type, then Long type)

(I use this OPC Connection: Ignition OPC UA Server, with a remote provider [Data_Edge])

I tried something like [API Puisard]DB21.DBD16
Then [API Puisard]DB21,DBD16

But it still doesn't work, can you help me? Thanks in advance!

Hi @Thomas_MUSSO ,

sometimes just reading the manual can learn you a lot :wink:

This one is not in the manual...

@Thomas_MUSSO
I believe that the correct address is:
[API Puisard]DB21,D16

For some reason siemens adds the DB in front of a bunch of data types.
You would change the D in D16 to match the data type you are reading from the PLC, so REAL16 if it was a float.

Correct but at least it give you the correct way to make your addressing.
DBXXX,DataTypeXXX

I've just checked in one of my project and we use the dword to read a UDINT
so the [API Puisard]DB21,D16 should work. In Ignition we used data type long.

Thank you for your reply Arnaud and David.

Concerning Float, addressing [API Puisard]DB21,REAL16 seems to work. Thanks !

However for UDINT (Ignition Data Type on “Long”), I try [API Puisard]DB21,DWORD16 -> don't work.

Then, for my BOOL, I try [API Puisard]DB21,DBX16.0 -> don't work.

I'll try to find out why. If you have any other ideas, I'd love to hear from you.

It should be [API Puisard]DB21,X16.0.

There is never a redundant "DB" in the address with this driver.

1 Like

[API Puisard]DB21,D16