OPC Item Path - ns=1;s=[Packer]DB20,DBW100 is not getting the tag data from the Siemens S7-1500.
Device Connections - The Siemens S7 shows Connected
Siemens Rack 0, slot 0
S7 Tag address - %DB20.DBW100 (INT)
Tried Data types W, I, D, DI, and DBW
more system info:
the PLC IP address is on a different subnet from the the Ignition server so the connection is thru an Edge Router X.
Ignition version 7.9
The Ignition driver adds the port 102
Port forwarding in the router does not include the :102
Tag Quality shows Bad or Error Configuration
The machine builder did not check the Activate OPC UA Client checkbox in TIA Portal. I discovered it after installing trial version of TIA. Been troubleshooting this for weeks. Nobody here knew enough about Ignition and Siemens. Thanks Phil, Phil