Simulation Aids where and orderBy expressions through IllegalArgumentException
@pturmel
I have the following expression:
unionAll(
	flatten(
		asList(
			asList(asList('Occurrence','str')),
			forEach(
				groupBy({this.custom.rawData},it()['path']),
				forEach(
					it()[1],
					asList(
						left(dateFormat(it()['timestamp'],'_hha'),4),
						"I"
			)[0]
	forEach(
		forEach(
			it()
		flatten(
			asList(
				asList(
					case(
						split(it()[0],'_',2)[0],
						'productlevel','No Product',
						'cap','No Caps',
						'downstream','Packaging',
						'No Bottles'
				forEach(it()[1],it()['value'])
This seems to produce a valid dataset although in vision if I run this in the designer I do get a ClassCastException: BasicDataset cannot be cast to class java.util.ArrayList.
The topic of this post is however, if I wrap this expression in either a where or an orderBy expression:
orderBy({expression above},descending(it()['Occurrence']))
where({expression above),it()['Occurrence'] = 'No Bottles')
I get an IllegalArgumentException: Wrong number of values for a row. Expected 25.
The same error is present for both Vision and perspective.
What am I doing wrong?
Additional information:
Sample Data
"#NAMES"
"path","value","quality","timestamp"
"#TYPES"
"str","L","I","date"
"#ROWS","120"
"productlevel_at_sp","0","192","2023-07-31 12:00:00.000"
"cap_supply","1","192","2023-07-31 12:00:00.000"
"downstream_stop_request","8","192","2023-07-31 12:00:00.000"
"empty_bottles_present","7","192","2023-07-31 12:00:00.000"
"empty_bottles_primied","5","192","2023-07-31 12:00:00.000"
"productlevel_at_sp","0","192","2023-07-31 13:00:00.000"
"cap_supply","2","192","2023-07-31 13:00:00.000"
"downstream_stop_request","5","192","2023-07-31 13:00:00.000"
"empty_bottles_present","3","192","2023-07-31 13:00:00.000"
"empty_bottles_primied","4","192","2023-07-31 13:00:00.000"
"productlevel_at_sp","5","192","2023-07-31 14:00:00.000"
"cap_supply","0","192","2023-07-31 14:00:00.000"
"downstream_stop_request","0","192","2023-07-31 14:00:00.000"
"empty_bottles_present","0","192","2023-07-31 14:00:00.000"
"empty_bottles_primied","1","192","2023-07-31 14:00:00.000"
"productlevel_at_sp","2","200","2023-07-31 15:00:00.000"
"cap_supply","0","192","2023-07-31 15:00:00.000"
"downstream_stop_request","1","192","2023-07-31 15:00:00.000"
"empty_bottles_present","0","192","2023-07-31 15:00:00.000"
"empty_bottles_primied","0","192","2023-07-31 15:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 16:00:00.000"
"cap_supply","2","192","2023-07-31 16:00:00.000"
"downstream_stop_request","2","192","2023-07-31 16:00:00.000"
"empty_bottles_present","0","192","2023-07-31 16:00:00.000"
"empty_bottles_primied","0","192","2023-07-31 16:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 17:00:00.000"
"cap_supply","3","192","2023-07-31 17:00:00.000"
"downstream_stop_request","13","192","2023-07-31 17:00:00.000"
"empty_bottles_present","0","192","2023-07-31 17:00:00.000"
"empty_bottles_primied","1","192","2023-07-31 17:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 18:00:00.000"
"cap_supply","3","192","2023-07-31 18:00:00.000"
"downstream_stop_request","11","192","2023-07-31 18:00:00.000"
"empty_bottles_present","0","192","2023-07-31 18:00:00.000"
"empty_bottles_primied","0","192","2023-07-31 18:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 19:00:00.000"
"cap_supply","5","192","2023-07-31 19:00:00.000"
"downstream_stop_request","7","192","2023-07-31 19:00:00.000"
"empty_bottles_present","4","192","2023-07-31 19:00:00.000"
"empty_bottles_primied","6","192","2023-07-31 19:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 20:00:00.000"
"cap_supply","5","192","2023-07-31 20:00:00.000"
"downstream_stop_request","1","192","2023-07-31 20:00:00.000"
"empty_bottles_present","5","192","2023-07-31 20:00:00.000"
"empty_bottles_primied","4","192","2023-07-31 20:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 21:00:00.000"
"cap_supply","2","192","2023-07-31 21:00:00.000"
"downstream_stop_request","0","192","2023-07-31 21:00:00.000"
"empty_bottles_present","0","192","2023-07-31 21:00:00.000"
"empty_bottles_primied","3","192","2023-07-31 21:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 22:00:00.000"
"cap_supply","2","192","2023-07-31 22:00:00.000"
"downstream_stop_request","1","192","2023-07-31 22:00:00.000"
"empty_bottles_present","1","192","2023-07-31 22:00:00.000"
"empty_bottles_primied","2","192","2023-07-31 22:00:00.000"
"productlevel_at_sp","0","200","2023-07-31 23:00:00.000"
"cap_supply","4","192","2023-07-31 23:00:00.000"
"downstream_stop_request","5","192","2023-07-31 23:00:00.000"
"empty_bottles_present","2","192","2023-07-31 23:00:00.000"
"empty_bottles_primied","3","192","2023-07-31 23:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 00:00:00.000"
"cap_supply","5","192","2023-08-01 00:00:00.000"
"downstream_stop_request","5","192","2023-08-01 00:00:00.000"
"empty_bottles_present","0","192","2023-08-01 00:00:00.000"
"empty_bottles_primied","3","192","2023-08-01 00:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 01:00:00.000"
"cap_supply","6","192","2023-08-01 01:00:00.000"
"downstream_stop_request","2","192","2023-08-01 01:00:00.000"
"empty_bottles_present","0","192","2023-08-01 01:00:00.000"
"empty_bottles_primied","2","192","2023-08-01 01:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 02:00:00.000"
"cap_supply","8","192","2023-08-01 02:00:00.000"
"downstream_stop_request","1","192","2023-08-01 02:00:00.000"
"empty_bottles_present","2","192","2023-08-01 02:00:00.000"
"empty_bottles_primied","3","192","2023-08-01 02:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 03:00:00.000"
"cap_supply","10","192","2023-08-01 03:00:00.000"
"downstream_stop_request","6","192","2023-08-01 03:00:00.000"
"empty_bottles_present","1","192","2023-08-01 03:00:00.000"
"empty_bottles_primied","3","192","2023-08-01 03:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 04:00:00.000"
"cap_supply","7","192","2023-08-01 04:00:00.000"
"downstream_stop_request","1","192","2023-08-01 04:00:00.000"
"empty_bottles_present","1","192","2023-08-01 04:00:00.000"
"empty_bottles_primied","3","192","2023-08-01 04:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 05:00:00.000"
"cap_supply","4","192","2023-08-01 05:00:00.000"
"downstream_stop_request","3","192","2023-08-01 05:00:00.000"
"empty_bottles_present","1","192","2023-08-01 05:00:00.000"
"empty_bottles_primied","3","192","2023-08-01 05:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 06:00:00.000"
"cap_supply","3","192","2023-08-01 06:00:00.000"
"downstream_stop_request","2","192","2023-08-01 06:00:00.000"
"empty_bottles_present","3","192","2023-08-01 06:00:00.000"
"empty_bottles_primied","6","192","2023-08-01 06:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 07:00:00.000"
"cap_supply","4","192","2023-08-01 07:00:00.000"
"downstream_stop_request","1","192","2023-08-01 07:00:00.000"
"empty_bottles_present","1","192","2023-08-01 07:00:00.000"
"empty_bottles_primied","1","192","2023-08-01 07:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 08:00:00.000"
"cap_supply","13","192","2023-08-01 08:00:00.000"
"downstream_stop_request","1","192","2023-08-01 08:00:00.000"
"empty_bottles_present","1","192","2023-08-01 08:00:00.000"
"empty_bottles_primied","1","192","2023-08-01 08:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 09:00:00.000"
"cap_supply","11","192","2023-08-01 09:00:00.000"
"downstream_stop_request","0","192","2023-08-01 09:00:00.000"
"empty_bottles_present","0","192","2023-08-01 09:00:00.000"
"empty_bottles_primied","2","192","2023-08-01 09:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 10:00:00.000"
"cap_supply","8","200","2023-08-01 10:00:00.000"
"downstream_stop_request","1","200","2023-08-01 10:00:00.000"
"empty_bottles_present","1","200","2023-08-01 10:00:00.000"
"empty_bottles_primied","6","200","2023-08-01 10:00:00.000"
"productlevel_at_sp","0","200","2023-08-01 11:00:00.000"
"cap_supply","0","200","2023-08-01 11:00:00.000"
"downstream_stop_request","0","200","2023-08-01 11:00:00.000"
"empty_bottles_present","0","200","2023-08-01 11:00:00.000"
"empty_bottles_primied","0","200","2023-08-01 11:00:00.000"
consoleOutput_from_traceMe.txt (78.0 KB)
Will have to study later (can't wait for me to implement pivot(), hmm?).
pivot() will be well worth the wait!
Doing my best to eliminate unnecessary script calls.
Straight-up bug, looks like. If you take the inner expression's resulting dataset as a constant to feed them, they break the same way. Will fix.
And fixed. For Ignition v8.1+ as usual: v2.0.8.232162051
I'm back.
Here is a clip of what I am seeing, this is also somewhat present in the client, but to a lesser extent.
designer
Error Stack Traces
NPE on Power Table.data
java.lang.Exception: Error executing expression binding on
Stop Occurances_New.Root Container.Group 1.Power Table 1.data
	at com.inductiveautomation.factorypmi.application.binding.ExpressionPropertyAdapter.runExpression(ExpressionPropertyAdapter.java:92)
	at com.inductiveautomation.factorypmi.application.binding.ExpressionPropertyAdapter$1.run(ExpressionPropertyAdapter.java:59)
	at com.inductiveautomation.ignition.client.util.EDTUtil$ProcessQueue.run(EDTUtil.java:126)
	at java.desktop/java.awt.event.InvocationEvent.dispatch(Unknown Source)
	at java.desktop/java.awt.EventQueue.dispatchEventImpl(Unknown Source)
	at java.desktop/java.awt.EventQueue$4.run(Unknown Source)
	at java.base/java.security.AccessController.doPrivileged(Native Method)
	at java.base/java.security.ProtectionDomain$JavaSecurityAccessImpl.doIntersectionPrivilege(Unknown Source)
	at java.desktop/java.awt.EventQueue.dispatchEvent(Unknown Source)
	at java.desktop/java.awt.EventDispatchThread.pumpOneEventForFilters(Unknown Source)
	at java.desktop/java.awt.EventDispatchThread.pumpEventsForFilter(Unknown Source)
	at java.desktop/java.awt.EventDispatchThread.pumpEventsForHierarchy(Unknown Source)
	at java.desktop/java.awt.EventDispatchThread.pumpEvents(Unknown Source)
	at java.desktop/java.awt.EventDispatchThread.run(Unknown Source)
Caused by: java.lang.RuntimeException: Unable to handle rowSource #2
	at com.automation_pros.simaids.expressions.UnionAll.execute(UnionAll.java:111)
	at com.inductiveautomation.ignition.client.expressions.ClientDynamicDispatchFunction.execute(ClientDynamicDispatchFunction.java:43)
	at com.inductiveautomation.ignition.common.expressions.FunctionExpression.execute(FunctionExpression.java:69)
	at com.inductiveautomation.ignition.common.expressions.DefaultFunctionFactory$ColumnRearrangeFunction.execute(DefaultFunctionFactory.java:1837)
	at com.inductiveautomation.ignition.common.expressions.functions.BaseFunction.executeAll(BaseFunction.java:64)
	at com.automation_pros.simaids.expressions.SimpleIterator.execute(SimpleIterator.java:177)
	at com.inductiveautomation.factorypmi.application.binding.ExpressionPropertyAdapter.runExpression(ExpressionPropertyAdapter.java:83)
	... 15 more
Caused by: java.lang.NullPointerException
	at com.automation_pros.simaids.expressions.UnionAll.buildWith(UnionAll.java:188)
	at com.automation_pros.simaids.expressions.UnionAll.execute(UnionAll.java:107)
	... 26 more
Ignition v8.1.24 (b2023011208)
Java: Azul Systems, Inc. 11.0.16.1
ClassCastException on summedData binding
Stop Occurances_New.Root Container.Group 1.Power Table 1.summedData
Caused by: java.lang.ClassCastException
ClassCastException on pivotedData
Stop Occurances_New.Root Container.Group 1.Power Table 1.pivotedData
NPE on Power Table 2.data
Stop Occurances_New.Root Container.Power Table 2.data
	at com.automation_pros.simaids.expressions.Flatten.execute(Flatten.java:55)
	at com.automation_pros.simaids.expressions.AsMap.execute(AsMap.java:41)
	at com.automation_pros.simaids.expressions.UnionAll.execute(UnionAll.java:52)
	... 15 more
Summary
Stop Occurances_New.Root Container.Power Table 2.effByHour
These errors also happen if I add/remove a custom property to/from one of the tables. Sometimes it seems to matter which order I refresh the bindings in. For instance if I refresh summed data prior to pivoted data, it will continue to show <No Data> until I have refreshed the pivoted data.
Sample Data
"#NAMES"
"#TYPES"
"#ROWS","120"
"Labeler","77","192","2023-08-10 13:00:00.000"
"Laber","0","192","2023-08-10 13:00:00.000"
"Caser","173","192","2023-08-10 13:00:00.000"
"Stacker","0","192","2023-08-10 13:00:00.000"
"Dynac","35","192","2023-08-10 13:00:00.000"
"Labeler","0","192","2023-08-10 14:00:00.000"
"Laber","107","192","2023-08-10 14:00:00.000"
"Caser","155","192","2023-08-10 14:00:00.000"
"Stacker","77","192","2023-08-10 14:00:00.000"
"Dynac","0","192","2023-08-10 14:00:00.000"
"Labeler","226","192","2023-08-10 15:00:00.000"
"Laber","0","192","2023-08-10 15:00:00.000"
"Caser","205","192","2023-08-10 15:00:00.000"
"Stacker","131","192","2023-08-10 15:00:00.000"
"Dynac","0","192","2023-08-10 15:00:00.000"
"Labeler","0","192","2023-08-10 16:00:00.000"
"Laber","0","192","2023-08-10 16:00:00.000"
"Caser","72","192","2023-08-10 16:00:00.000"
"Stacker","0","192","2023-08-10 16:00:00.000"
"Dynac","18","192","2023-08-10 16:00:00.000"
"Labeler","0","192","2023-08-10 17:00:00.000"
"Laber","0","192","2023-08-10 17:00:00.000"
"Caser","877","192","2023-08-10 17:00:00.000"
"Stacker","134","192","2023-08-10 17:00:00.000"
"Dynac","14","192","2023-08-10 17:00:00.000"
"Labeler","0","192","2023-08-10 18:00:00.000"
"Laber","0","192","2023-08-10 18:00:00.000"
"Caser","0","192","2023-08-10 18:00:00.000"
"Stacker","35","192","2023-08-10 18:00:00.000"
"Dynac","0","192","2023-08-10 18:00:00.000"
"Labeler","3","192","2023-08-10 19:00:00.000"
"Laber","29","192","2023-08-10 19:00:00.000"
"Caser","312","192","2023-08-10 19:00:00.000"
"Stacker","0","192","2023-08-10 19:00:00.000"
"Dynac","14","192","2023-08-10 19:00:00.000"
"Labeler","0","192","2023-08-10 20:00:00.000"
"Laber","35","192","2023-08-10 20:00:00.000"
"Caser","121","192","2023-08-10 20:00:00.000"
"Stacker","0","192","2023-08-10 20:00:00.000"
"Dynac","0","192","2023-08-10 20:00:00.000"
"Labeler","0","192","2023-08-10 21:00:00.000"
"Laber","178","192","2023-08-10 21:00:00.000"
"Caser","47","192","2023-08-10 21:00:00.000"
"Stacker","0","192","2023-08-10 21:00:00.000"
"Dynac","0","192","2023-08-10 21:00:00.000"
"Labeler","0","192","2023-08-10 22:00:00.000"
"Laber","0","192","2023-08-10 22:00:00.000"
"Caser","116","192","2023-08-10 22:00:00.000"
"Stacker","0","192","2023-08-10 22:00:00.000"
"Dynac","0","192","2023-08-10 22:00:00.000"
"Labeler","68","192","2023-08-10 23:00:00.000"
"Laber","0","192","2023-08-10 23:00:00.000"
"Caser","17","192","2023-08-10 23:00:00.000"
"Stacker","0","192","2023-08-10 23:00:00.000"
"Dynac","0","192","2023-08-10 23:00:00.000"
"Labeler","0","192","2023-08-11 00:00:00.000"
"Laber","0","192","2023-08-11 00:00:00.000"
"Caser","29","192","2023-08-11 00:00:00.000"
"Stacker","0","192","2023-08-11 00:00:00.000"
"Dynac","25","192","2023-08-11 00:00:00.000"
"Labeler","0","192","2023-08-11 01:00:00.000"
"Laber","36","192","2023-08-11 01:00:00.000"
"Caser","106","192","2023-08-11 01:00:00.000"
"Stacker","0","192","2023-08-11 01:00:00.000"
"Dynac","0","192","2023-08-11 01:00:00.000"
"Labeler","0","192","2023-08-11 02:00:00.000"
"Laber","0","192","2023-08-11 02:00:00.000"
"Caser","24","192","2023-08-11 02:00:00.000"
"Stacker","0","192","2023-08-11 02:00:00.000"
"Dynac","18","192","2023-08-11 02:00:00.000"
"Labeler","113","192","2023-08-11 03:00:00.000"
"Laber","0","192","2023-08-11 03:00:00.000"
"Caser","131","192","2023-08-11 03:00:00.000"
"Stacker","0","192","2023-08-11 03:00:00.000"
"Dynac","67","192","2023-08-11 03:00:00.000"
"Labeler","0","192","2023-08-11 04:00:00.000"
"Laber","0","192","2023-08-11 04:00:00.000"
"Caser","137","192","2023-08-11 04:00:00.000"
"Stacker","0","192","2023-08-11 04:00:00.000"
"Dynac","0","192","2023-08-11 04:00:00.000"
"Labeler","102","192","2023-08-11 05:00:00.000"
"Laber","90","192","2023-08-11 05:00:00.000"
"Caser","38","192","2023-08-11 05:00:00.000"
"Stacker","0","192","2023-08-11 05:00:00.000"
"Dynac","34","192","2023-08-11 05:00:00.000"
"Labeler","25","192","2023-08-11 06:00:00.000"
"Laber","0","192","2023-08-11 06:00:00.000"
"Caser","588","192","2023-08-11 06:00:00.000"
"Stacker","0","192","2023-08-11 06:00:00.000"
"Dynac","0","192","2023-08-11 06:00:00.000"
"Labeler","0","192","2023-08-11 07:00:00.000"
"Laber","0","192","2023-08-11 07:00:00.000"
"Caser","157","192","2023-08-11 07:00:00.000"
"Stacker","0","192","2023-08-11 07:00:00.000"
"Dynac","0","192","2023-08-11 07:00:00.000"
"Labeler","317","192","2023-08-11 08:00:00.000"
"Laber","50","192","2023-08-11 08:00:00.000"
"Caser","793","192","2023-08-11 08:00:00.000"
"Stacker","0","192","2023-08-11 08:00:00.000"
"Dynac","0","192","2023-08-11 08:00:00.000"
"Labeler","111","192","2023-08-11 09:00:00.000"
"Laber","0","192","2023-08-11 09:00:00.000"
"Caser","811","192","2023-08-11 09:00:00.000"
"Stacker","18","200","2023-08-11 09:00:00.000"
"Dynac","0","192","2023-08-11 09:00:00.000"
"Labeler","174","192","2023-08-11 10:00:00.000"
"Laber","229","192","2023-08-11 10:00:00.000"
"Caser","549","192","2023-08-11 10:00:00.000"
"Stacker","0","200","2023-08-11 10:00:00.000"
"Dynac","0","192","2023-08-11 10:00:00.000"
"Labeler","162","200","2023-08-11 11:00:00.000"
"Laber","231","200","2023-08-11 11:00:00.000"
"Caser","534","192","2023-08-11 11:00:00.000"
"Stacker","0","200","2023-08-11 11:00:00.000"
"Dynac","0","200","2023-08-11 11:00:00.000"
"Labeler","0","200","2023-08-11 12:00:00.000"
"Laber","0","200","2023-08-11 12:00:00.000"
"Caser","0","192","2023-08-11 12:00:00.000"
"Stacker","0","200","2023-08-11 12:00:00.000"
"Dynac","0","200","2023-08-11 12:00:00.000"
Pivoted Data Expression
columnRearrange(
	unionAll(
		flatten(
			asList(
				forEach(
					groupBy({Root Container.Group 1.Power Table 1.historicalData},it()['path']),
					forEach(
						it()[1],
						asList(
							left(dateFormat(it()['timestamp'],'_ha'),if(len(dateFormat(it()['timestamp'],'_ha')) = 4,3,4)),
							"F"
				)[0]
		forEach(
			forEach(
				groupBy(
					it()['path']
				it()
			flatten(
				asList(
					asList(it()[0]),
					forEach(it()[1],round(it()['value'] / 60.0,1))
	'Occurrence',
	'_7A',
	'_8A',
	'_9A',
	'_10A',
	'_11A',
	'_12P',
	'_1P',
	'_2P',
	'_3P',
	'_4P',
	'_5P',
	'_6P',
	'_7P',
	'_8P',
	'_9P',
	'_10P',
	'_11P',
	'_12A',
	'_1A',
	'_2A',
	'_3A',
	'_4A',
	'_5A',
	'_6A'
Summed Data Expression
selectStar(
	{Root Container.Group 1.Power Table 1.pivotedData},
	asMap(
		forEach(
			groupBy(
				{Root Container.Group 1.Power Table 1.last8HistoricalData},
				it()['path']
			asList(
				it()[0],
				round(sum(it()[1],'value')/60.0,1)
	)[it()['Occurrence']],
	'Last 8',
	'F',
	asMap(
		forEach(
			groupBy(
				it()['path']
			asList(
				it()[0],
				round(sum(it()[1],'value') / 60.0,1)
	'Last 24',
	'F'
So, null pointer exceptions are always a bug. This update prevents those two, and provide more helpful information where available:
For Ignition v8.1+: v2.0.9.232231702
For the class cast exceptions, you will need to configure your designer launcher to include this extra JVM option:
-XX:-OmitStackTraceInFastThrow
That will cause a more complete stack track to be reported.
Updated to 2.0.9, included JVM option.
NPE
Stop Occurances_New.Root Container.Group.Power Table.data
at com.inductiveautomation.factorypmi.application.binding.ExpressionPropertyAdapter.startup(ExpressionPropertyAdapter.java:113)
at com.inductiveautomation.factorypmi.application.binding.DefaultInteractionController.startupBindings(DefaultInteractionController.java:355)
at com.inductiveautomation.factorypmi.application.binding.DefaultInteractionController.startupAdapters(DefaultInteractionController.java:360)
at com.inductiveautomation.factorypmi.application.FPMIWindow.startup(FPMIWindow.java:346)
at com.inductiveautomation.factorypmi.designer.workspace.WindowWorkspace$DesigntimeWindowOpener.openWindow(WindowWorkspace.java:3791)
at com.inductiveautomation.factorypmi.designer.workspace.WindowWorkspace.openWindow(WindowWorkspace.java:1520)
at com.inductiveautomation.factorypmi.designer.workspace.WindowWorkspace$4.lambda$createPanels$2(WindowWorkspace.java:628)
at com.inductiveautomation.ignition.designer.workspacewelcome.RecentlyModifiedTilePanel$Tile.lambda$new$1(RecentlyModifiedTilePanel.java:206)
at com.inductiveautomation.ignition.client.util.gui.Listen$1.mousePressed(Listen.java:52)
at java.desktop/java.awt.AWTEventMulticaster.mousePressed(Unknown Source)
at java.desktop/java.awt.Component.processMouseEvent(Unknown Source)
at java.desktop/javax.swing.JComponent.processMouseEvent(Unknown Source)
at java.desktop/java.awt.Component.processEvent(Unknown Source)
at java.desktop/java.awt.Container.processEvent(Unknown Source)
at java.desktop/java.awt.Component.dispatchEventImpl(Unknown Source)
at java.desktop/java.awt.Container.dispatchEventImpl(Unknown Source)
at java.desktop/java.awt.Component.dispatchEvent(Unknown Source)
at com.jidesoft.docking.DockingUtils.a(Unknown Source)
at com.jidesoft.docking.DefaultDockingManager.handleEvent(Unknown Source)
at com.jidesoft.docking.DefaultDockingManager$a3.eventDispatched(Unknown Source)
at java.desktop/java.awt.Toolkit$SelectiveAWTEventListener.eventDispatched(Unknown Source)
at java.desktop/java.awt.Toolkit$ToolkitEventMulticaster.eventDispatched(Unknown Source)
at java.desktop/java.awt.Toolkit.notifyAWTEventListeners(Unknown Source)
at java.desktop/java.awt.KeyboardFocusManager.redispatchEvent(Unknown Source)
at java.desktop/java.awt.DefaultKeyboardFocusManager.typeAheadAssertions(Unknown Source)
at java.desktop/java.awt.DefaultKeyboardFocusManager.dispatchEvent(Unknown Source)
at java.desktop/java.awt.EventQueue$5.run(Unknown Source)
at com.automation_pros.simaids.expressions.ColumnsOf.execute(ColumnsOf.java:30)
... 70 more
Class Cast Exception on summedData
Caused by: java.lang.ClassCastException: class com.inductiveautomation.ignition.common.BasicDataset cannot be cast to class java.util.ArrayList (com.inductiveautomation.ignition.common.BasicDataset is in unnamed module of loader java.net.URLClassLoader @1529fea1; java.util.ArrayList is in module java.base of loader 'bootstrap')
	at com.automation_pros.simaids.expressions.GroupBy.accumulateOutput(GroupBy.java:106)
	at com.automation_pros.simaids.expressions.SimpleIterator.execute(SimpleIterator.java:212)
	at com.automation_pros.simaids.expressions.IterationHelper.condSubstExpression(IterationHelper.java:249)
	at com.automation_pros.simaids.expressions.IterationHelper.preExecuteAll(IterationHelper.java:165)
	at com.automation_pros.simaids.expressions.IterationHelper.condSubstExpression(IterationHelper.java:205)
	at com.automation_pros.simaids.expressions.SimpleIterator.execute(SimpleIterator.java:206)
	... 15 more
Class Cast Exception on effByHour
	at com.automation_pros.simaids.expressions.InnerJoin.execute(InnerJoin.java:140)
	... 15 more
Class Cast Exception on pivotedData
Stop Occurances_New.Root Container.Group.Power Table.pivotedData
	at com.inductiveautomation.ignition.common.expressions.SubscriptExpression.execute(SubscriptExpression.java:50)
	at com.automation_pros.simaids.expressions.AsList.execute(AsList.java:39)
	at com.automation_pros.simaids.expressions.Flatten.execute(Flatten.java:37)
	... 15 more
Thanks for the detailed report. Found and fixed a stale data bug in groupBy(). Also fixed the NPE in columnsOf(). (The null source was the failures in groupBy, as far as I can tell.)