Hi, I have tried to use a SQLite DB for my application. I have the problem with a Historian Tag on version 8.0.16 version on Windows 10 enterprise 64 bit.
My tag is stored even 30s. If I open the DB I view a correct data . But in table and chart no. There is a problem with SQLite?
Something strange going on:
>>> print system.date.fromMillis(-519269173L)
Thu Dec 25 18:45:30 EST 1969
If you look at the settings for the SQLite JDBC Driver (Gateway > Config > Databases > Drivers > edit “SQLite”, is the Driver Type set to something other than SQLITE?
For transparency, we found an issue where the Driver Type was incorrectly set to GENERIC. New installations shouldn’t run into this anymore, but it seems possible to upgrade into this state (as you found). If this is the case, then switching the Driver Type to SQLITE and saving should take care of the issue.
No, i have the settings in generic. I try. Thank,s