Standard Deviation issue
I have a table with the following numbers
4.577
4.578
4.578
4.578
4.578
4.578
4.579
4.580
4.579
4.579
4.580
4.578
4.581
4.582
4.582
4.581
4.581
4.582
4.581
4.571
4.569
If I use the StDev(tablename,data,“numbers”)
I get this number
0.00321208
If I use a sql statement
I get this number
0.00339408
When I use minitab or excel I get this number
0.003291403
any ideas why its so different?
Without spending a lot of time digging, a couple of possibilities come to mind.
First is rounding. Are those numbers exactly 3 decimal places, or being displayed as three decimal places? Obviously any calculation using the full number of decimal places can be different than a calculation using a rounded number.
Also, there are two types of standard deviation, sample and population, and their results will be different. Ignition’s stdDev expression function uses sample standard deviation.
For grins, I plugged the data you posted into Wolfram Alpha. I got 0.00321208 as the sample std dev and 0.0032914 as the population std dev. No idea how sql is getting its number unless rounding is coming into play.
I’m rounding all the numbers to 3 decimal places. Thank you for your response