system.tag.editTag problem
I tried to used “system.tag.editTag”, but It does not work in my case.
I have one tag and one data type that I want to disable in the “Tag_Test” folder.
This is the code in the value change of “tag”:
system.tag.editTag(tagPath="[default]Tag_Test/Tag1", overrides={"STATUS":{"Enabled":"false"}})
I tried to change the value in this tag but the data type “Tag8” It is not disabled.
I enclose an image.
How can I solve it?
Try -
system.tag.editTag(tagPath="[default]Tag_Test/Tag1", attributes={"Enabled":"False"})
Overrides are used for editing tags within the UDT, you are trying to edit the UDT itself so you would think of it as a tag and use attributes instead. Just a note - in the manual example it uses “STATUS” as the override key, STATUS would be the name of the tag within the UDT that you are overriding.
Thanks you very much! Now it works.
Andrea