Tag Change Script on Fixed Rate Question
I have a tag that is configured to have its execution mode set at a fixed rate with an execution rate of 1 min (60,000 ms). I then have another tag that acts as a rate of change tag for this fixed rate tag. This rate of change tag receives its value from a value change script set on the fixed tag.
My question is: If the fixed tag’s value doesn’t change, will the tag change script still run after a minute? If the fixed tag doesn’t have a value change after a min, then it’s rate of change after a minute should be 0, but I am not sure if the value change script will run and if the current value and previous value will be the same.
The valueChange script will not run if there's no change.
So if I want to calculate the rate of change after 1 minute even without a change in value, could I use the quality change script? Perhaps the timestamp property of the tag will change given the fixed rate execution mode which will activate the quality change script?
If you want to execute a script every 60 seconds consider a timer script.
I have to admit that I would immediately use my Integration Toolkit's recorder(), set to two rows at 60000ms, in an expression tag, to do this with no script at all.