Tag from plc not coming out on opc server

I created OPC tags that already existed in PLC. Then I made a new PLC tag in the PLC and it does not come out. I tried several new tags and none of them come out. I have been doing this for months and never had this issue. PLC tag is active and running in PLC

Assuming you’re using a Logix driver, try going to Config->OPC-UA->Devices on the Ignition gateway web page and then tap More->Refresh Browse (if available) next to the PLC device. Otherwise, tap Edit next to PLC device, and then Save on the following page.

1 Like

Got it and worked thank you.