Tag historical sample rate

Hi guys,

I am struggling with the historical sample rate, I have set the mode to periodic and 10 seconds sample rate at a minimum. But why I am getting 20s and 30s or even more sample rate?
image

Cheers
Johnny

Try changing the Historical Deadband to 0.


Hi there, thanks for your reply, I changed the mode to “on change” and deadband to 0 , still min sample rate is not at 10 s .

I think what is happening is the value isn’t changing so you aren’t satisfying the deadland condition. Changing to on change i would expect similar results.

I see I see , yup deadband to 0 and periodic mode would do the job. Thank you so much !

1 Like