Tag Status Rollup
I must be missing something, this should be simple.
We have a UDT with an integer status tag calculated on the device. I currently have about 75 of those devices, but will end up with several hundred. The UDT also includes a parameter that categorizes the devices. What I’m trying to do is find the worst case status in each category. Pseudo code:
For each Instance in folder:
    category = Instance.parameter.category
    category_status = run some code here based on Instance.statustag.value
I can deal with all the code except for the “for each Instance…”, that part is throwing me for a loop. I figure there has to be a function or feature that allows me to find all the instances/tags in a folder and iterate through them.
Suggestions gratefully accepted.
You can use system.tag.browse.
https://docs.inductiveautomation.com/display/DOC81/system.tag.browse
This will go through each tag in “folder1”, you can filter the results to your liking.
paths = []
folder1tags = system.tag.browse(path = '[default]Folder1')
for folder1tag in folder1tags.getResults():
	paths.append(str("[default]Folder1/" + folder1tag['name']))
system.tag.browse or system.tag.configure?
Edit: @josborn beat me to it.