The context is Ignition Edge 8.1 on Ubuntu linux.
We have two copper Ethernet connections that take separate paths to connect to a central network. The path connected to one is preferred because it is faster. We want to monitor the status of each path by determining if a central server can be reached.
This function almost works reliably.
def PingCheck2(source, dest):
# Ping destination IPv4 address through
# network interface with source IPv4 address
# Both source and dest string
# Returns true if ICMP ping succeeds
from java.net import InetAddress
from java.net import NetworkInterface
try:
ip1 = InetAddress.getByName(source)
netif = NetworkInterface.getByInetAddress(ip1)
ip2 = InetAddress.getByName(dest)
if netif != None:
return ip2.isReachable(netif, 0, 10000)
else:
return False
except:
return False
This doesn't quite work because it is sensitive to routes even though you would think routes are to be ignored if the interface is being specified.
If no explicit route to the server is in the routes table, this works for the preferred interface, which has a lower metric for the general 0.0.0.0 route.
Kernel IP routing table
Destination Gateway Genmask Flags Metric Ref Use Iface
0.0.0.0 192.168.99.94 0.0.0.0 UG 20010 0 0 enp6s0
0.0.0.0 192.168.133.1 0.0.0.0 UG 20050 0 0 enp7s0
169.254.0.0 0.0.0.0 255.255.0.0 U 1000 0 0 enp6s0
192.168.99.80 0.0.0.0 255.255.255.240 U 10 0 0 enp6s0
192.168.133.0 0.0.0.0 255.255.255.0 U 50 0 0 enp7s0
However, it fails for the second interface even though a command line ping -I with the network interface specified works fine. The java isReachable() method returns nothing until I add a static route through the slower interface. Once that is added the test for the primary path becomes unreliable, working some of the time.
192.168.0.0 192.168.133.1 255.255.255.0 UG 50 0 0 enp7s0
If a route is present for each connection, it only works for the entry with the lower metric.
Is anyone aware of a workaround for this? Ping -I at the shell command works as expected but isReachable() fails in this condition.
Thanks,