Hello Everyone,
I am seeing a tickmanager entries non stop the message says:
“Aggregate callback time exceeded tick rate x > 250ms “
x is a number greater than 250.
Any ideas on what the issue will be or how to prevent this message from showing on the logs ?
You could turn the logger off, but otherwise it looks like the only thing to do might be slow down the sampling interval of some of the tags configured @ 250ms.
How far beyond 250ms are your x values? There must be a lot of Monitored Items @ 250ms for this warning to trigger.
Thanks @Kevin.Herron , will this be the configuration set on the Tag groups ? If so there is no groups configured at 250ms
External OPC UA clients? Simulator or TCP devices? Not sure what else would cause this...
Transaction groups with OPC items?