Hello everyone,
Thank you in advance for your time and insights on this topic. I am looking to control an integer tag on a PLC that represents different modes of program operation, with values ranging from 1 to 5. Specifically, a value of 2 indicates "Manual Mode."
I need to implement a toggle switch on the user interface that allows users to switch between "Auto" and "Manual." The desired behavior is as follows:
  • When the tag is set to 2, the toggle switch should indicate "Manual."
  • When the tag is set to 1, 3, 4, or 5, the toggle switch should indicate "Auto."
Additionally, I require this link to be bi-directional:
  • If the toggle switch is set to "Auto" and you change it to "Manual," the tag should set to 2.
  • Conversely, if the toggle switch is set to "Manual" and you change it to "Auto," the tag should set to 1.
I would appreciate any guidance on the best approach to establish this functionality.
Thank you!
Use a multi-state button.
Use two states, one with text Manual and value 2, one with text Auto and value 1
For the controlValue bind this to your tag with Bidirectional set to true.
For the indicatorValue, bind it to your tag, add transform, select script, use this script
	if value > 2:
		return 1
	return value
I agree that a multistate button is the appropriate component for this.
However, I'd change the indicatorValue binding to an expression binding:
if ({this.props.controlValue} = 2, 2, 1)
Thanks Victor, works the best!
I appreciate it.
Thanks Pascal for the hint. I'll use it.