I am using a transaction group within Ignition 7.6.3.
I have three essentially identical transaction groups for three pieces of equipment. Two of them dont have errors but the one does.
Here is one of the two ones not producing an error
Here is the one producing an error..
The one producing an error is going back and forth between running and errored. I am not positive if its going back and between running and errored when the Trigger tag is going back and forth between True and False.
Any thoughts?
Anything in the Events tab?
Looks like its getting value of NULL sometimes.
I am watching the tag and I see nothing but going back and forth between true and false
My bad...its related to the Start_Time...hmmm
It might not be an issue. Even though the trigger is cycling on and off every second per the plc program, its not actually started so I can see why the Start_Time is blank. The other two also show Start_Time as NULL as they too aren't started yet. I am thinking once the triggers for the other two get activated they would show the same thing if the trigger is active but its technically not started.
To me the trigger shouldn't be turning on unless you are running but this is an older program by another programmer.
Yes, that version of Ignition is somewhere around 15 years old.
How is start time defined? What do you see if you double click on that tag in the transaction?