Trouble using tag value in tag event script
I have the following code as a tag event script on a temperature tag
	value = int(currentValue.value)
	tagPath = "[~]_Sample_Device_/Writeable/WriteableBoolean1.value"
	lowerLimit = system.tag.read("[~]lowerLimit.value")
	upperLimit = system.tag.read("[~]upperLimit.value")
	if value > upperLimit:
		system.tag.writeAsync([tagPath], [0])
	elif value < lowerLimit:
		system.tag.writeAsync([tagPath], [1])
I’m trying to get the code to use two number entry boxes to set an upper/lower limit at which to switch on/off a heater.
The above code is not working but if I replace the limits in the code with numbers like this:
	if value > 28:
	elif value < 23:
It works.
What am I doing wrong?
system.tag.read() return a QualityValue so you need to .value
and .value its not needed in the tagpath
	tagPath = "[~]_Sample_Device_/Writeable/WriteableBoolean1"
	lowerLimit = system.tag.read("[~]lowerLimit").value
	upperLimit = system.tag.read("[~]upperLimit").value
That worked, thanks.
Happy to help^^