Trouble with Modbus tags

Hello, I'm working on a project to set up power monitoring station in Ignition. I'm having trouble connecting to tags. My device is connect to the OPC network. I read somewhere that I might have configured the device wrong from the start. The device I'm trying to connect to is the PowerLogic ION 7550.

Here's the mapping I found for it


and here's the error I keep getting in ignition

Any help would be amazing

Check your unit ID setup for the modbus comms, IE if it is 1 instead of 0, try this
[PWM1]1.HRUS40150

2 Likes

Try these addresses:

  • HR150
  • 1.HR150
  • 1.HR40150
2 Likes

This form is amazing. It worked and thank you for the help!

1 Like

Which one :smiley:

Technically both. however, the address that didn't have the 40k in front was the value I wanted

the 1.HR150 for clarification

2 Likes